How many power points can a dental surgery have?
There is no cap on the number of outlets in a dental surgery or treatment room. The limit is on the safety switch: one 10 mA RCD can protect no more than 12 points, and a point is a socket-outlet or a piece of hard-wired equipment. So a room with more outlets isn’t a problem, it simply needs more RCDs, and they sit in the room with the rest.
The dental chair and any imaging equipment count as points too, but each usually has its own dedicated circuit and RCD, so they don’t use up the twelve on the room’s general outlets. The cleaners’ outlet is separate again, on its own circuit from the switchboard with its own 10 mA RCD.
The useful thing is to decide where the outlets go before the walls close: the bench, the imaging wall, the chair, charging points for handpieces and screens. Adding them afterwards means opening walls and retesting the room.
Related
- The RCD rules, with section numbers
- What a new dental surgery needs electrically
- The fit-out checklist
Not quite your question? Ask it and we may answer it as a page.
Rules in your state
Pick your state
See who certifies and inspects there.
More questions
- What does a new dental surgery need electrically?
- Do I need an electrician to move a dental chair?
- How often does a medical or dental room need electrical testing?
- What is the green sign in a dental surgery or treatment room?
- Can a GP consult room be used for ECGs?
- Who certifies the electrical work in a dental or medical fit-out?
Need an electrician who does this?
Other states and New Zealand
Pick your state for its rules and the electricians listed there, or ask us to find one. Electricians and builders can get listed.
LND Group is the site publisher’s own business. How listings work.